Hi Team,
I have been trying to install the Software-Add-on - PC WORX TARGET FOR SIMULINK - 2400041 on my PC, I download the two available versions 2400041_1.40 and 2400041_1.42, both in compressed files, version 1.42 when trying to unzip it appears to me that it has been downloaded with error already tried several times.
System requirements for creating the model in Matlab Simulink asks me this: Visual Studio 2016 Pro ver, Matlab R2016a, Matlab Coder+Simulink Coder.
I have instaled Visual Studio 2019 and MATLAB R2020a, and at the time of the installation of 2400041_1.40 I get the following screen where it tells me that it is not possible to continue with the installation because the minimum requirements are missing: MATLAB R2016a + Simulink + Simulink coder..
You know how I can solve this situation, I have problems due to the versions of: Visual Studio 2019 and MATLAB R2020a?
I appreciate your help and comments in advance.
Regards
Cesar Torres