Hello,
Attempting to use the AXL SE DI16/1 smart element for digital inputs.

- D light on AXC is flashing red
- D 1-4 on the AXL F BP SE4 are all solid red
- WBM showing "Failed to list local bus modules" and error codes
- wmb local bus.png

This is how the modules are set up:
engineer.png
Attachments (2)
Eduard PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello charkrit,

the failure means, that your configured AXIO-Bus in PLCnext Engineer and the physical configuration on the AXCF2152 are diffrent, please check the axio devices and the order in the busconfiguration first.
It can also be a HW-failure (pin of axio.device is bent), in this case please try to add the axio modules successively (in PLCnext Engineer Project and physical axio busconfiguration) and start your application with limited axio-bus (to isolate the cause of error).

I hope I could help you, if not please send me a feedback.

Best Regards
Eduard
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
charkrit Accepted Answer Pending Moderation
0
Votes
Undo
I have reviewed the order that they are connected and the order in the configuration.

This is how it is currently configured.
busconfig.png PXL_20210322_005704742.MP.jpg

I am receiving the same error codes and behavior from the status LEDs.
Attachments (2)
Betina Jessen Accepted Answer Pending Moderation
0
Votes
Undo
Great. :D
charkrit Accepted Answer Pending Moderation
0
Votes
Undo
I am still receiving errors with the AXL F BP SE4 module. Is there something wrong with my configuration?
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello Charkrit,
yes you have a SE SC configured but have a SE SC-A in place.
there is a difference between these modules please adapt your configuration to SC-A
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
juankax Accepted Answer Pending Moderation
0
Votes
Undo
Hi Oliver, thanks for the help.