Hello,

I am using a AXC F 2152(2404267) in combination with the IF CAN (2702668). The purpose of the unit is to receive, combine and send CAN-bus data. The data combining is done with general application code base on "C" this is compolied in the C++ code that is running on the PLC. All of this is working but there is a problem with the CAN-bus data processing.

We get and send data to the IF CAN by ArpPlcGds_BeginRead and ArpPlcGds_BeginWrite. After some debugging I descovered that these command consume more then 6ms. This is a problem to support CAN-bus data at 250kbs 50% busload. The main loop speed is ~60MHz.

Is there any other way how to exces this CAN-bus data at at least 500us?

Arpversion:
21.0.5.35585

Example:

// Read data from a fieldbus input frame
void SmartLinkPlcCanDriver::readPortData(char* pValue, size_t valueSize)
{
if(!this->_initAxioline) {
return;
}

TGdsBuffer* gdsBufferCanIn;
size_t offsetCanIn;

if(!ArpPlcIo_GetBufferPtrByPortName("Arp.Io.AxlC", IO_PORT_IN, &gdsBufferCanIn)) {
Log::Error("ArpPlcIo_GetBufferPtrByPortName in failed");
return;
}

if(!ArpPlcGds_GetVariableOffset(gdsBufferCanIn, IO_PORT_IN, &offsetCanIn)) {
Log::Error("ArpPlcGds_GetVariableOffset in failed");
return;
}

// Begin read operation, memory buffer will be locked
char* readDataBufferPage;
if(ArpPlcGds_BeginRead(gdsBufferCanIn, &readDataBufferPage))
{
// Copy data from GDS buffer
char* dataAddress = readDataBufferPage + offsetCanIn;
memcpy(pValue, dataAddress, valueSize);

// Unlock buffer
if(!ArpPlcGds_EndRead(gdsBufferCanIn))
{
Log::Error("ArpPlcGds_EndRead failed");
}
}
else
{
Log::Error("ArpPlcGds_BeginRead failed");
ArpPlcGds_EndRead(gdsBufferCanIn);
}

// Release the GDS buffer and free internal resources
if(gdsBufferCanIn != NULL)
{
if(!ArpPlcIo_ReleaseGdsBuffer(gdsBufferCanIn))
{
Log::Error("ArpPlcIo_ReleaseGdsBuffer failed");
}
}
}


Wilco.
Who is viewing this page
Eduard PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello Wilco,

I see in code, you are using the direct access to AXIO-Frame (CAN-Process Data), do you also tried to define the ports and connect it in PLCnEng with CAN processdata via GDS?
//#port
//#attributes(Input)
uint8 PD_IN[64];

//#port
//#attributes(Output)
uint8 PD_OUT[64];

In the fist Step I would like to recommend you to connect the process Data via GDS and start the Cpp-program in 1ms Task. The goal should be to send/receive the CAN-Data in 1ms cyclic.
Second step: AXC F 2152(2404267) allows to start 1ms-Tasks, If you would like to use 500us Task, you can use the AXC F 3152 controller with more performance.

I hope it helps, if not please send me a short feedback.

Best Regards
Eduard
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
mgenergysystems Accepted Answer Pending Moderation
0
Votes
Undo
Hello Eduard,

Thanks for your quick response!

I have created a new test project in Eclipse under windows, DownloadLink zip file for workspace with example code. In the end it is working like I had expected. Along the way I discovered that the 1ms Log::Info handling caused a task handling delay of ~70 ms each ~140ms. Probably because it has to be written to flash at some point. Solved this "debuging" problem by putting the debug information in the transmitting CAN-bus messages :)

So with the PLC it is possible to handle 100% busload :)

Next step is to implement my own application code that is written in C. Still problems with this.
Added *.c compile option to CMakeLists.txt (not in example code) this solved to problem to compile C code. But gives me a multiple definition of `main' problem. See below for build output.

When I remove the SHARED option in the CMakeList.txt it is possible to build but then gives problems with deploying:
add_library(SmartLinkPlc SHARED${Headers} ${Sources})
cmd.exe /c ""C:\Program Files\PHOENIX CONTACT\PLCnCLI\/plcncli.exe" deploy -p"C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc" -b Release -t"AXCF2152,2021.0.5 LTS (21.0.5.35585)" -s"src""
No library file was found in the path 'C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc\bin\AXCF2152_21.0.5.35585\Release'.

Can you help me with this are could you sudgest me an other approch to make this work?
I have application code that only require some platform functions like send and receive CAN-bus messages beside this there are also some I/O's that we have to set and read. The application I have at the moment is running in a while condition, this could be adjusted to a cyclic task function.



cmd.exe /c ""C:\Program Files\PHOENIX CONTACT\PLCnCLI\/plcncli.exe" generate code -p"C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc" -s"src""
Generating all files with the 'code' generator for C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc.
Successfully generated all files with the 'code' generator for C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc.

cmd.exe /c ""C:\Program Files\PHOENIX CONTACT\PLCnCLI\/plcncli.exe" generate config -p"C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc" -s"src""
Generating all files with the 'config' generator for C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc.
Successfully generated all files with the 'config' generator for C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc.

cmd.exe /c ""C:\Program Files\PHOENIX CONTACT\PLCnCLI\/plcncli.exe" build -p"C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc" -b Release -t"AXCF2152,2021.0.5 LTS (21.0.5.35585)""
Requested build for targets AXCF2152,21.0.5.35585
Starting build for target AXCF2152,21.0.5.35585
Checking if CMake needs to be reconfigured...
[cmake]:
[cmake]: C:\workspacesEclipse2021\SmartLinkPlc\SmartLinkPlc\intermediate\cmake\AXCF2152,21.0.5.35585\Release>set PATH=C:\Program Files\eclipse\plugins\PLCnCLI_SDK_2021.0.5_LTS_Windows_AXC_F_2152\sysroots\x86_64-pokysdk-mingw32\usr\bin;C:/Users/Wilco/.p2/pool/plugins/org.eclipse.justj.openjdk.hotspot.jre.full.win32.x86_64_16.0.1.v20210528-1205/jre/bin/server;C:/Users/Wilco/.p2/pool/plugins/org.eclipse.justj.openjdk.hotspot.jre.full.win32.x86_64_16.0.1.v20210528-1205/jre/bin;C:\Program Files (x86)\Common Files\Oracle\Java\javapath;C:\Python\Python37\Scripts\;C:\Python\Python37\;C:\WINDOWS\system32;C:\WINDOWS;C:\WINDOWS\System32\Wbem;C:\WINDOWS\System32\WindowsPowerShell\v1.0\;C:\WINDOWS\System32\OpenSSH\;C:\Program Files\PuTTY\;C:\WINDOWS\system32\config\systemprofile\.dnx\bin;C:\Program Files\Microsoft DNX\Dnvm\;C:\Program Files\Microsoft SQL Server\130\Tools\Binn\;C:\Program Files\Microsoft VS Code\bin;C:\Program Files\dotnet\;C:\Program Files\Git\cmd;C:\Qt\Tools\QtCreator\lib;C:\Program Files (x86)\ConfuserEx;C:\Program Files (x86)\Flash Magic;C:\Program Files (x86)\IVI Foundation\VISA\WinNT\Bin\;C:\Program Files\IVI Foundation\VISA\Win64\Bin\;C:\Program Files (x86)\IVI Foundation\VISA\WinNT\Bin;C:\Program Files\TortoiseSVN\bin;C:\Program Files\Nordic Semiconductor\nrf-command-line-tools\bin\;C:\Program Files (x86)\Vector CANdb++ 3.1\Exec32;C:\Program Files (x86)\dotnet\;C:\Users\Wilco\AppData\Local\Microsoft\WindowsApps;C:\Users\Wilco\AppData\Local\GitHubDesktop\bin;C:\Program Files (x86)\Flash Magic;;C:\Users\Wilco\AppData\Local\Microsoft\WindowsApps;C:\Users\Wilco\.dotnet\tools;C:\Program Files\PHOENIX CONTACT\PLCnCLI\;C:\Users\Wilco\eclipse\cpp-2021-06\eclipse;
[cmake]: make[1]: Entering directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: make[2]: Entering directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: Scanning dependencies of target SmartLinkPlc
[cmake]: make[2]: Leaving directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: make[2]: Entering directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: [ 2%] Building C object CMakeFiles/http://SmartLinkPlc.dir/CMakeFiles/3.13.1/CompilerIdC/CMakeCCompilerId.c.o
[cmake]: [ 4%] Building C object CMakeFiles/http://SmartLinkPlc.dir/CMakeFiles/feature_tests.c.o
[cmake]: [ 7%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/intermediate/code/SmartLinkPlcComponent.meta.cpp.o
[cmake]: [ 9%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/intermediate/code/SmartLinkPlcComponentProgramProvider.cpp.o
[cmake]: [ 11%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/intermediate/code/SmartLinkPlcLibrary.cpp.o
[cmake]: [ 14%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/intermediate/code/SmartLinkPlcLibrary.meta.cpp.o
[cmake]: [ 16%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/src/SmartLinkPlcComponent.cpp.o
[cmake]: [ 19%] Building CXX object CMakeFiles/http://SmartLinkPlc.dir/src/SmartLinkPlcProgram.cpp.o
[cmake]: [ 21%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/builds/smartlink_mx/services_implementation/buzzer/buzzer.c.o
[cmake]: [ 23%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/builds/smartlink_mx/services_implementation/can/can.c.o
[cmake]: [ 26%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/builds/smartlink_mx/services_implementation/notify/notify.c.o
[cmake]: [ 28%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/builds/smartlink_mx/services_implementation/platform/platform.c.o
[cmake]: [ 30%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/builds/smartlink_mx/services_implementation/timer/timer.c.o
[cmake]: [ 33%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/MQTT/MQTT.c.o
[cmake]: [ 35%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/average_filter/average_filter.c.o
[cmake]: [ 38%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/battery_information/battery_information.c.o
[cmake]: [ 40%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/battery_ratings/battery_ratings.c.o
[cmake]: [ 42%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/cJSON/cJSON.c.o
[cmake]: [ 45%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/coffee_can/coffee_can.c.o
[cmake]: [ 47%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/crc_ccitt/crc_ccitt.c.o
[cmake]: [ 50%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/crc_stream/crc_stream.c.o
[cmake]: [ 52%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/event_storage/event_storage.c.o
[cmake]: [ 54%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/ftoa/ftoa.c.o
[cmake]: [ 57%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/item_queue/item_queue.c.o
[cmake]: [ 59%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/list/list.c.o
[cmake]: [ 61%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/master_information/master_information.c.o
[cmake]: [ 64%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/memory_stream/memory_stream.c.o
[cmake]: [ 66%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/platform/platform.c.o
[cmake]: [ 69%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/qrcodegen/qrcodegen.c.o
[cmake]: [ 71%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/queue/queue.c.o
[cmake]: [ 73%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/shared_stream/shared_stream.c.o
[cmake]: [ 76%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/storage_tester/storage_tester.c.o
[cmake]: [ 78%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/stream/stream.c.o
[cmake]: [ 80%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/tasks/tasks.c.o
[cmake]: [ 83%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/time_provider/time_provider.c.o
[cmake]: [ 85%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/trace/trace.c.o
[cmake]: [ 88%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/transition/transition.c.o
[cmake]: [ 90%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/unit_test/unit_test.c.o
[cmake]: [ 92%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/value_conversion/value_conversion.c.o
[cmake]: [ 95%] Building C object CMakeFiles/http://SmartLinkPlc.dir/src/services/value_storage/value_storage.c.o
[cmake]: [ 97%] Linking CXX shared module libSmartLinkPlc.so
[cmake]: make[2]: Leaving directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: c:/program files/eclipse/plugins/plcncli_sdk_2021.0.5_lts_windows_axc_f_2152/sysroots/x86_64-pokysdk-mingw32/usr/bin/arm-pxc-linux-gnueabi/../../libexec/arm-pxc-linux-gnueabi/gcc/arm-pxc-linux-gnueabi/9.3.0/real-ld.exe: CMakeFiles/http://SmartLinkPlc.dir/CMakeFiles/feature_tests.c.o: in function `main':
[cmake]: feature_tests.c:(.text.startup+0x0): multiple definition of `main'; CMakeFiles/http://SmartLinkPlc.dir/CMakeFiles/3.13.1/CompilerIdC/CMakeCCompilerId.c.o:CMakeCCompilerId.c:(.text.startup+0x0): first defined here
[cmake]: collect2.exe: error: ld returned 1 exit status
[cmake]: make[2]: *** [CMakeFiles/http://SmartLinkPlc.dir/build.make:693: libSmartLinkPlc.so] Error 1
[cmake]: make[1]: *** [CMakeFiles/Makefile2:73: CMakeFiles/http://SmartLinkPlc.dir/all] Error 2
[cmake]: make[1]: Leaving directory 'C:/workspacesEclipse2021/SmartLinkPlc/SmartLinkPlc/intermediate/cmake/AXCF2152,21.0.5.35585/Release'
[cmake]: make: *** [Makefile:130: all] Error 2
cmake process exited with error


Eclipse IDE for C/C++ Developers
Version: 2021-06 (4.20.0)
Build id: 20210612-2011
PLCnext Technology C++ 21.0.0.489 com.phoenixcontact.plcnext.cplusplus.feature.feature.group PHOENIX CONTACT GmbH & Co. KG
  1. one week ago
  2. PLCnext Engineer
  3. # 2
  • Page :
  • 1


There are no replies made for this post yet.
However, you are not allowed to reply to this post.