Has anyone been successful setting up an AXC F 2152 with the Interbus adapter and safety bridge modules?
I can get DO16 and DI16 modules working, but have been unsuccessful with safety bridge modules. I've attached an image to show the error codes.
Attachments (1)
Automation Engineer - MI, USA
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hi Rob,

We have confirmation that this does work OK.

Important:
Baudrate DIP-Switches must be correct.
MODE DIP-Switches must be correct.
Addressing DIP-Switches must be correct.
Please take care not to mix up ON and OFF on these switches.

If you need more information, please let us know - perhaps we can contact you by email to check the details of your project.

(ref: #219766)
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
Rob H Accepted Answer Pending Moderation
0
Votes
Undo
I had the incorrect settings for Baudrate and Mode. I was able to get it working with those corrected. Thank you.