It appears that the BF-C and BF-D LEDs will flash when there is no Profinet network configured, even if the project does not require a Profinet network.

For my current project, I would like to stop these LEDs from flashing red, since the customer may think that flashing red LEDs indicate an error.

What is the recommended way to stop these LEDs from flashing red, in situations where a Profinet network is not required?

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support

Accepted Answer
jkustan@phoenixcon.com Accepted Answer Pending Moderation
1
Votes
Undo

My colleague Yuri showed me this:

I like to use vim to edit files, so type vim AXCF2152.acf.settings and then i for insert once the file opens. Change the following from true to false:

To save and exit, shift+zz. Next, reboot. Upon reboot, your red LED should be no more. I assume if you want to use Profinet at some point, this needs to be changed back to true.

atroyas@phoenixcontact.es Accepted Answer Pending Moderation
0
Votes
Undo

Hi,

I have the same problem. I have a project with in which I don´t need to use Profinet and PN Controller and PN Device Led´s are flashing red.

Is it possible to deactive them?

 

Thanks

 

Frank PLCnext Team Accepted Answer Pending Moderation
1
Votes
Undo

Hi Martin, Angel,

currently it is not possible to deactivate the LEDs out of PC Worx Engineer, but we know this requirement (as it is already possible with PC Worx 6 with many PLCs).

I'll check if it is possible to deactivate the LEDs as temporary solution over a few config files...

Cause many collegues are still on vacation this could take a while.

Cu

Frank


Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support

fblanchard Accepted Answer Pending Moderation
0
Votes
Undo

@Frank: Is it solved now with the latest PCWE v7.2.2 ?

Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello,

this feature was rescheduled for the next PC Worx Engineer release after the SPS IPC Drives this year.

In that version (7.3) alot new features will be included.

 

Edit: Yes the whole package of configurable PN-D and PN-C ect. was moved to the next release at SPS IPC Drives

Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support