  1. dhoysan
  2. Proficloud
  3. Friday, 31 January 2020

Hi,

I was wondering if there is any limits on the range of registers the Cloud IoT Gateway can read from?

I have a customer using with data spread across registers 40001 to 40198. The customer is claiming that data communication stops around register 40100. This could be related to his hardware, however I also wanted to check to see if this could be a limitation of the Cloud IoT Gateway.

Let me know your thoughts.

Thanks,

Dave

Accepted Answer
Arno PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi Dave,

there is no limit on the range of registers the Cloud IoT Gateway can read from. For example with the EMPros we used 50000 and higher.

 


Phoenix Contact Electronics Headquarter - Support Center

dhoysan Accepted Answer Pending Moderation
0
Votes
Undo

After speaking more with customer, it sounds like the issue is with his other hardware and not the gateway. Please disregard the original question, unless there is a limit that I should be aware of.

Thanks,

Dave