Store PLCnext CommunityPLCnext on LinkedInPLCnext on Instagram  PLCnext on YouTube Github PLCnext CommunityStore PLCnext Community

  1. gh.lee
  2. PLCnext Store
  3. Thursday, 26 November 2020

Our customer installed Codesys Control for AXC F 2152 and they tried to add AXL SE modules in Codesys Control software.

As you can see the attached files, there is no information for AXL SE.

Would you please how to add AXL SE modules in Codesys Control software?

Thank you for your support.

Have a nice day.

Attachments (3)
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello,

It looks like the definitions for AXL SE modules are not included in your Codesys installation.

Someone from Codesys will need to tell you how to add I/O module definitions to a Codesys installation.

Regards,
Martin.

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support

  1. more than a month ago
  2. PLCnext Store
  3. # 1
gh.lee Accepted Answer Pending Moderation
0
Votes
Undo

Hi, Martin

Is there any device description file of AXL SE for Codesys?

If I can get the file, I will try to add it.

 

  1. more than a month ago
  2. PLCnext Store
  3. # 2
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Yes, please go to the product page for the device you are using, e.g.:

https://phoenixcontact.com/product/1088127

(for AXL SE DI16/1)

In the "Downloads" section, there is a Device Description file for that article. I don't know if this works with Codesys - if you are unsure, you will need to check with Codesys.

~ Martin.

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support

  1. more than a month ago
  2. PLCnext Store
  3. # 3
Andrew Ellis Accepted Answer Pending Moderation
0
Votes
Undo

I don't know if this is still an issue. But just to make everyone aware, Smart elements have been added to the latest COEDSYS package for PLC Next:

 

https://store.codesys.com/codesys-control-for-plcnext-sl.html?___SID=U

 

So if you download and install (update) to the V4.0.0 package, then you should have the option to add Smart elements to the Axioline bus in CODESYS.

  1. 2 weeks ago
  2. PLCnext Store
  3. # 4
  • Page :
  • 1


There are no replies made for this post yet.
However, you are not allowed to reply to this post.