  1. gian.flores
  2. PLCnext Technology & PLCnext Controls
  3. Wednesday, 10 March 2021
I downloaded the project sources to the plc to allow other programmers upload capability. The project is now complete and we would like to not provide the sources to our customer. Is there a way to delete the project sources in the plc so it can't be uploaded.
Accepted Answer
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello Gian,
as soon as you download the project without sources the projectsources will be gone from the PLC.
you can make sure by checking like this:



root@axcf2152:/opt/plcnext# find . -name "*pcweax"

./projects/PCWE/Src/Test.pcweax
./backup/PCWE/Src/Test.pcweax

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support