I have an EPC1522 and created a project with PLCnext Engineer. I have an AXL F BK PN in my network. I can integrate and configure the BK with PLCnext Engineer but after downloading the project to the EPC, the Profinet diagnosis shows that the Profinet communication is lost. The same happens with a Profinet switch. What am I missing? Sending a ping to the BK works.
Attachments (1)
Accepted Answer
Stefan Brinkmann Accepted Answer Pending Moderation
0
Votes
Undo
The problem is solved now. I was not aware that only Port X3 works for Profinet. There was nothing in the manuals. Finally I found a clue in the WBM.