Hi,

I exported variables from PLC data list and then tried to import them to another project but only the safety variables were imported.
Is this a known issue?

Br Stefan
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
please check with 2021.6 the following parameters ?
It was not reprodcable to see the behavior you had explained.
Both types of variables can be imported by the softkey.

inline1625264903.png

(ref: #219098)
Attachments (1)
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
Stefan Svanbäck Accepted Answer Pending Moderation
0
Votes
Undo
Hi,
Thanks for the reply.

I found the issue that caused the problem. When a data type is missing no variables are imported to the non safe plc.
The pop-up does not clarify the problem but in log in project tab it is shown

Br Stefan

Screenshot 2021-09-08 070745.png
Attachments (1)
  • Page :
  • 1


There are no replies made for this post yet.