  1. al-mukhtar
  2. PLCnext Technology & PLCnext Controls
  3. Monday, 06 September 2021
Hi everyone , iwas able to find the plcnext through the ethernet wire connection, but i can't find the plcnext throughWi-Fi, (yes i turn on either the Wi-Fi or lan one at time), any suggestionsor settings that i should add .
Im using laptop with windows10 and plcnext 2021.6 firmware
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
When you say "find the plcnext", do you mean:

1. find the PLC in the Search window in PLCnext Engineer?
2. Connect to the PLC from PLCnext Engineer?
3. Open an SSH connection to the PLC from a Windows command prompt?

For (1), please check:
- the correct adapter is selected in the drop-down list in the Project -> Online Controllers window.

2021-09-08_8-59-53.jpg

- the WiFi device is a Layer 2 device. The DCP protocol used to discover PLCnext Control devices is a layer 2 protocol, so cannot be routed.
- If these don't work, you could try assigning the required IP address to the PLC using the direct cable connection, and then switch to WiFi for programming.

For (2), please check:
- the correct adapter is selected in the drop-down list in the Project -> Online Controllers window.
- The IP address of the PC's WiFi adapter is in the same subnet as the PLC.

For (3), please check:
- The IP address of the PC's WiFi adapter is in the same subnet as the PLC.
Attachments (1)