Hi,

A connection to the Cloud is not possible with the CLOUD IOT GATEWAY (1031235), when a Gateway-address is registered on eth0 (LAN / ETH2 Local) and eth1 (WAN / ETH1 Internet) use DHCP.

iot gw

The IOT-Gateway can connected to the internet in two ways:

1.) Network Interface eth1 ("ETH1 Internet" Connector) the IOT-Gateway is a router => LAN Default Gateway should be empty.

2.) Network Interface eth0 ("ETH2 Local" Connecter) the IOT-Gateway is a one legged router => It has a LAN Default Gateway and the ETH1 Internet is not connected.

 iot gateway

Something is confusing: It seem that Internet and Local is mixed up in the documentation.

network iotgw

Thanks

Frank PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
The issue was reolved in call 119143
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
  1. more than a month ago
  2. Proficloud
  3. # 1
Sorin Dumitriu - Sidoflux Accepted Answer Pending Moderation
0
Votes
Undo
The issue was reolved in call 119143

This link is no longer active. I have a similar issue as described above.
  1. more than a month ago
  2. Proficloud
  3. # 2
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Here is the feedback from the original poster:

The main problem was a registered gateway on the lan side (eth0 local).
Without the gateway setting the communication to the cloud works.
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
  1. more than a month ago
  2. Proficloud
  3. # 3
Sorin Dumitriu - Sidoflux Accepted Answer Pending Moderation
0
Votes
Undo
Hi Martin!

As I understood from the original post, there is the possibility to connect the eth0/local interface to a router which have Internet access and leave the eth1/Internet unconnected with DHCP address and have both Proficloud connection and WUI access from remote?
Can you confirm?
Thanks!
  1. more than a month ago
  2. Proficloud
  3. # 4
Arno PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello,
normally this is not possible. The local LAN is for Modbus and the webUI. The connection to proficloud is establisched over ETH1.

Regards, Arno
Phoenix Contact Electronics Headquarter