Dear colleagues, I am writing to you because I have some doubts regarding a request made by a client who is working with PLCNext, which I will tell you about below:

- How can I have 4 clients connected via Modbus TCP to a PLCNext working as a Modbus TCP server?

What do you suggest?

Accepted Answer
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello,

If you want to use PLCnext Engineer exclusively, then one option is to use four instances of the Modbus/TCP Server function block, each one bound to a different port. Each of the four clients will then need to connect to one of the four ports on the server.

If you would prefer to implement a Modbus server in C++, you will not necessarily be restricted to one client connection per port, but this requires intermediate-to-advanced C++ programming skills.

You can also check if any PLCnext Store apps might help, e.g. Codesys seems to implement a Modbus Server, and perhaps that allows muliple client connections on a single server port.

Hope this helps.

~ Martin.

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support