EN ENO

Hello,

 I began with the new software PLCnext Engineer, I consult them where I find the option to condition the blocks, example.
the coparations, mathematical operations, move, etc. I have attached a screenshot of where I found this on PCworx. this to better explain my query. Thanks ..

 

Accepted Answer
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi Carlos,

This feature is currently planned for PLCnext Engineer version 2021.0, due for release at the end of this year.

Until then, it is possible to achieve a similar outcome using a SEL block after the block you would like to enable/disable.

Something like this:

2020 05 23 14 41 29

~ Martin.

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support