Hello,

I have an AXC F 2152 running 2021.0.3 LTS on which, according to both PLCnext Engineer and htop, the memory usage increases from around 45% on startup to 99% over a period of about 10 minutes. Once it reaches 99%, it wavers a bit between 98% and 99%.

According to htop, the top memory users are three instances of `/usr/sbin/syslog-ng`, each of which are using up about 21.6%. The rest is many instances of `Arp.System.Application`

Starting/stopping the PLC runtime doesn't affect this at all, only a reboot seems to reset the memory usage. Is there any advice on figuring out why this is happening, or a way to turn down the logging level?

Thank you,

John Crummy
Accepted Answer
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
I've disabled logging in nginx by modifying the `access_log` line in the nginx.conf file by commenting out the existing line and then adding a line to disable logging.


#access_log syslog:server=unix:/dev/log,facility=auth,tag=nginx,nohostname,severity=info combined;
access_log off;


So far my memory use has remained constant (besides the usual up and down bit), even when running our custom app. The PLC has also remained responsive.

I think this has solved the problem, but I will check over the weekend to make sure it remains stable for multiple days.

Thank you, Oliver, for pointing me in the right direction.
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
I should have mentioned that this seems to be causing the PLC to reboot periodically, about once every 20 minutes or so.
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
After some more testing, the problem doesn't seem to be with `syslog-ng`. On subsequent reboots, the problem remains, however `syslog-ng` is not the main user of memory, `Arp.System.Application` is. Also, the time until the memory hits 99% full is on the order of 20-30 minutes, no the 10 minutes I indicated above.
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello John,

you can check the contents of the logs to see what causes the high amount of memory.
-> are you writing large amounts of Data to log?
check the Size of your Output.log?


ls -lah /opt/plcnext/logs/Output.log


Did you configure the Datalogger to write not often enough to file?

please provide the output of this command:

ps --sort -rss -eo pid,pmem,rss,vsz,comm | head -16


Check the size of the RAM disks with :

df -hal

tpmfs 245M 101M 145M 41% /var
tmpfs 245M 160K 245M 1% /run

if it is the RAM disk that is occupied by to many files
find the large files on RAM.

du -a /var/ | sort -n -r | head -n 20
du -a /run/ | sort -n -r | head -n 20


If it realy is the Arp.System.Application that is allocating a lot of ram my guess is that there is a memoryleak in one of the Libraries you are using.
Are you using your own C++ code?
which libraries are you using?

kind regards,
Oliver
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
Hi Oliver,

For Output.log, it is 8.7M at the moment.

Command outputs:

$ ps --sort -rss -eo pid,pmem,rss,vsz,comm | head -16
PID %MEM RSS VSZ COMMAND
1518 21.3 107040 672052 Arp.System.Appl
1213 10.9 54788 82056 syslog-ng
1558 7.7 38776 219912 Arp.System.Appl
1559 3.3 16964 153312 Arp.System.Appl
1452 1.9 9536 11676 nginx
1525 1.5 7592 40416 rauc
1450 1.3 6748 8928 nginx
1451 1.3 6724 8924 nginx
1449 1.3 6584 8800 nginx
1453 1.2 6432 8684 nginx
5109 1.1 5764 8176 sshd
1207 0.9 4516 8932 ntpd
5113 0.8 4120 5520 bash
1232 0.7 3960 123440 lttng-sessiond
5112 0.7 3924 8176 sshd
$ df -hal
Filesystem Size Used Avail Use% Mounted on
tpmfs 245M 245M 0 100% /var/volatile
/dev/root 365M 275M 67M 81% /media/rfs/ro
/dev/mmcblk0p6 488M 182M 271M 41% /media/rfs/rw
overlay 488M 182M 271M 41% /
/dev/mmcblk0p6 488M 182M 271M 41% /media/rfs/internalsd
proc 0 0 0 - /proc
sysfs 0 0 0 - /sys
debugfs 0 0 0 - /sys/kernel/debug
configfs 0 0 0 - /sys/kernel/config
devtmpfs 245M 412K 245M 1% /dev
tmpfs 245M 120K 245M 1% /run
/dev/mmcblk0p7 27M 431K 25M 2% /etc/device_data
devpts 0 0 0 - /dev/pts
cgroup 245M 0 245M 0% /sys/fs/cgroup
cgroup 0 0 0 - /sys/fs/cgroup/cpuset
cgroup 0 0 0 - /sys/fs/cgroup/cpu
cgroup 0 0 0 - /sys/fs/cgroup/cpuacct
cgroup 0 0 0 - /sys/fs/cgroup/blkio
cgroup 0 0 0 - /sys/fs/cgroup/memory
cgroup 0 0 0 - /sys/fs/cgroup/devices
cgroup 0 0 0 - /sys/fs/cgroup/freezer
cgroup 0 0 0 - /sys/fs/cgroup/net_cls
cgroup 0 0 0 - /sys/fs/cgroup/net_prio
cgroup 0 0 0 - /sys/fs/cgroup/pids
cgroup 0 0 0 - /sys/fs/cgroup/rdma
name=systemd 0 0 0 - /sys/fs/cgroup/systemd
$ du -a /var/volatile | sort -n -r | head -n 20
250864 /var/volatile
250844 /var/volatile/log
150620 /var/volatile/log/auth.log
99968 /var/volatile/log/auth.log.2
68 /var/volatile/log/syslog
64 /var/volatile/log/messages
44 /var/volatile/log/user.log
24 /var/volatile/log/kern.log
16 /var/volatile/log/dmesg
12 /var/volatile/tmp
8 /var/volatile/tmp/AxlC.config.svc
8 /var/volatile/log/debug
8 /var/volatile/log/boot
4 /var/volatile/tmp/tmpfile
4 /var/volatile/log/wtmp
4 /var/volatile/log/nginx/pxcapi.error.log
4 /var/volatile/log/nginx
4 /var/volatile/log/lastlog
4 /var/volatile/log/error
4 /var/volatile/log/daemon.log


I'm not using the datalogger at all, and the only library I'm using is the "PLCnext Controller" library. No C++ running. I did have a custom program running in Linux userspace, but I've kept it from running for now, and the problem remains.

The PLC did not reboot last night (uptime is around 18 hours now), however the memory use remains at 99%.

Looking at the contents of the `/var/volatile` folder, it seems that the `auth.log` (and `auth.log.2`) are massive, and quite possible what are causing the problem. The one thing I was doing was using the HTTP REST interface to monitor things, and I see that the `auth.log` file seems to log every single request I made to the REST interface. Is that normal? Is the a way to disable that logging?

For the REST interface, I'm using the variables endpoint and polling regularly, should I be doing something different? I see that there is support for sessions, but the documentation doesn't really make it clear what the benefits of that are, except that you attach a session ID to everything.

Thank you,

John
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
I will add that by simply deleting `auth.log` and `auth.log.2` my memory usage dropped immediately to 84%.
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello John,
good to hear that you found a solution.
Can you per chance show me some of the typical entries that cause the issue for you?
I hope we can reduce this impact in future.

kind regads,
Oliver
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
Oliver,

First off, I can confirm that the PLC stayed alive over the weekend (uptime is 2 days, 20 hours), and memory usage is steady, so this definitely looks solved.

The log entries are all of the form:


Apr 26 08:20:39 axcf2152 nginx: 10.23.16.10 - - (26/Apr/2021:08:20:39 -0700) "GET /_pxc_api/v1.2/variables?pathPrefix=http://Arp.Plc.Eclr/&paths=(LONG LIST OF VARIABLE NAMES) HTTP/1.1" 200 9690 "-" "Go-http-client/1.1"


NOTE: The '(' and ')' in the snippet above are actually '[' and ']'. I had to change them otherwise my reply wouldn't show up. I don't know how to escape the square brackets.

There is one for each request to that endpoint from our tool (written in Go, as you can see). Because this tools polls frequently, these entries add up quickly.

John
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello John,
thank you for the details.
Okay so your client is polling a long list of variables.
Thats why the log file is flooding so quickly.

We will fix this log mechanism in the next version.

There are some features in the rest interface that optimize this pollings Sessions + Variablegroups.
-> You register a group of variables and then only poll a specific group. (this also circumvents the issue of limited)
Thats what the ehmi does.
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
johncrummy Accepted Answer Pending Moderation
0
Votes
Undo
Thanks, Oliver. I will have to take a look at using sessions and groups when I get a chance. My list of variables changes depending on what a user is looking at at any one time, which is why I didn't use them initially, but I think with a bit of work I can implement the groups.