Using AXC F2152 Firmware 2021.6. Was connecting to the proficloud on Friday with no problem. Was unable to connect today - MQTT error. Rebooting and re-downloading program did not remove error. I did a Type 1 reset and added certificate. I still cannot connect and have new error. Screen captures attached

Proficloud error.jpg
Attachments (1)
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Only for Firmware >= 2021.6:
After the Type 1 reset the private key required for the Proficloud.io connection gets lost on the device. To enable the device to request the private key again from the platform please click "Reset Token" in the Device Management Service. After the re-rollout is enabled for 10min.
(ref: #217026)
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
  1. more than a month ago
  2. Proficloud
  3. # 1
Sidnei Marcondes Accepted Answer Pending Moderation
0
Votes
Undo
Hi Martin,

I have exactly the same problem. I have tried to Reset the Token. But the PLCnext still present the same error (There is no valid private key on the device).
Do you have another suggestion ?

Thank you

Sidnei
  1. more than a month ago
  2. Proficloud
  3. # 2
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
The problem was solved by downgrading the firmware to 2021.0.5, connecting the PLC to Proficloud, then upgrading to FW 2021.6, after which the PLC kept the connection to Proficloud.
(ref: #217379)
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support