Hello:

 

Are there instructions for installing an 'Offline' App that is downloaded as a file onto my PC ?

 

I was able to download the file to the PC... what are the next steps to install on the AXC F 2152 ?

 

Thank you !!

 

Peter

ahiraoka Accepted Answer Pending Moderation
0
Votes
Undo

Hello Peter,

 

You can install apps via WBM of the target device.

At the bottom of left side on the website, you can see "Administration - PLCnext Apps", which is added newly.

 

  1. more than a month ago
  2. PLCnext Store
  3. # 1
DanielK PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello Peter,

as ahiraoka already said you can install the app via the WBM. 

There are three steps to do an offline installation for an PLCnext app: In the frist step you go to the PLCnext Store and select your app. Then download this app to your PC. In the second step you must connect your PC to the PLCnext Control and go to the WBM. There is a chapter called Adminstation with a subchapter PLCnext Apps. In this area you can upload the app. After this the installtion you can start or stop the app.

If the app is licensed (=costs money) you must perform a small handshake process to bind the license to your PLCnext Control.

 

Best regards,

Daniel

  1. more than a month ago
  2. PLCnext Store
  3. # 2