Hello Sir

PLCnext Engineer software always couldn't be open as normal, could you help me ?and the report list is as follow:

PLCnext_Engineer_couldnt_open_as_normal.JPG

PLCnext Engineer, Version 2020.0.1 (Build 4.0.266.0)

Unexpected Exception
======================================================================
The composition produced a single composition error. The root cause is provided below. Review the CompositionException.Errors property for more detailed information.

1) Object reference not set to an instance of an object.

Resulting in: One or more errors occurred.

Resulting in: An exception occurred while calling the 'OnImportsSatisfied' method on type 'Ade.ApplicationControl.ApplicationControlServerComponent'.

Resulting in: Cannot activate part 'Ade.ApplicationControl.ApplicationControlServerComponent'.
Element: Ade.ApplicationControl.ApplicationControlServerComponent --> Ade.ApplicationControl.ApplicationControlServerComponent --> AssemblyCatalog (Assembly="Ade.ApplicationControl.ContractsImpl, Version=4.0.266.0, Culture=neutral, PublicKeyToken=55558f70c9068f5b")

Resulting in: Cannot get export 'Ade.ApplicationControl.ApplicationControlServerComponent (ContractName="Ade.Components.IStartupModule")' from part 'Ade.ApplicationControl.ApplicationControlServerComponent'.
Element: Ade.ApplicationControl.ApplicationControlServerComponent (ContractName="Ade.Components.IStartupModule") --> Ade.ApplicationControl.ApplicationControlServerComponent --> AssemblyCatalog (Assembly="Ade.ApplicationControl.ContractsImpl, Version=4.0.266.0, Culture=neutral, PublicKeyToken=55558f70c9068f5b")

 

Exception chain:
----------------------------------------------------------------------
CompositionException

======================================================================

Details
----------------------------------------------------------------------

CompositionException
==============================
Message:
------------------------------
The composition produced a single composition error. The root cause is provided below. Review the CompositionException.Errors property for more detailed information.

1) Object reference not set to an instance of an object.

Resulting in: One or more errors occurred.

Resulting in: An exception occurred while calling the 'OnImportsSatisfied' method on type 'Ade.ApplicationControl.ApplicationControlServerComponent'.

Resulting in: Cannot activate part 'Ade.ApplicationControl.ApplicationControlServerComponent'.
Element: Ade.ApplicationControl.ApplicationControlServerComponent --> Ade.ApplicationControl.ApplicationControlServerComponent --> AssemblyCatalog (Assembly="Ade.ApplicationControl.ContractsImpl, Version=4.0.266.0, Culture=neutral, PublicKeyToken=55558f70c9068f5b")

Resulting in: Cannot get export 'Ade.ApplicationControl.ApplicationControlServerComponent (ContractName="Ade.Components.IStartupModule")' from part 'Ade.ApplicationControl.ApplicationControlServerComponent'.
Element: Ade.ApplicationControl.ApplicationControlServerComponent (ContractName="Ade.Components.IStartupModule") --> Ade.ApplicationControl.ApplicationControlServerComponent --> AssemblyCatalog (Assembly="Ade.ApplicationControl.ContractsImpl, Version=4.0.266.0, Culture=neutral, PublicKeyToken=55558f70c9068f5b")

 

Stack trace:
------------------------------
at System.ComponentModel.Composition.Hosting.CompositionServices.GetExportedValueFromComposedPart(ImportEngine engine, ComposablePart part, ExportDefinition definition)
at System.ComponentModel.Composition.Hosting.CatalogExportProvider.GetExportedValue(CatalogPart part, ExportDefinition export, Boolean isSharedPart)
at System.ComponentModel.Composition.Primitives.Export.get_Value()
at System.ComponentModel.Composition.ExportServices.GetCastedExportedValue[T](Export export)
at System.Lazy`1.CreateValue()
at System.Lazy`1.LazyInitValue()
at Ade.Components.ComponentFramework.a()
at Ade.Diagnostics.ApplicationEventSource.<>c__DisplayClass8_0.b__0()
at Ade.Diagnostics.ApplicationEventSource.RunAction[T](String category, String actionName, Func`1 action)
at Ade.Diagnostics.ApplicationEventSource.RunAction(String category, String actionName, Action action)
at Ade.Components.ComponentFramework.Init()
at Ade.UIFramework.MainControl..ctor()
at (PCWorxNextApplicationStarter )
at PCWorxNext.PCWorxNextApplicationStarter.CreateMainWindow()
at Ade.Application.ApplicationStarter.Init()
at (String[] )
at PCWorxNext.Startup.Main(String[] args)

 

Eduard PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello,

I would like to recommend you to uninstall the PLCnext Engineer 2020.0.1, install the last version 2020.3 and try to open your project again.

Please send me a short feedback, if the problem can be resolved or not.

Thanks & Best Regards

Eduard


Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support

602129929@qq.com Accepted Answer Pending Moderation
0
Votes
Undo

Hello Sir ,unfortunately,even worse, I couldn't install 2020.3 PLCnext engineer at all. And the prompt message is very limited . So could you help me to anysls it?2020.3_failed.JPG

 

 

602129929@qq.com Accepted Answer Pending Moderation
0
Votes
Undo

Hello Sir ,unfortunately,even worse, I couldn't install 2020.3 PLCnext engineer at all. And the prompt message is very limited . So could you help me to anysls it?

Attachments (1)
Frank PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi,

I've spoken with the dev department.

It seems that this issue is quite often related to some user rights and or some virus scanners, they suggested me the following:

  • Deinstall PLCnext Eng
  • Delete the user config files (/users/youruser/AppData/Roaming/Phoenix Contact/PLCnext Engineer/Version/user.config
  • Deactivate your virus scanner
  • Reinstall PLCnext Eng with Admin privileges
  • Start PLCnext Eng with Admin priviliges

Keep also in mind that you need Windows 10 64Bit!

If this still not help please contact your local Phoenix Contact sales representative to get in direct contact with you.

Reg

Frank


Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support