When I try to select ethernet to connect PLCnext Engineer to my PLC, I see red cross. I actually see this red cross for all options except "Wi-FI Intel(R) Dual Band Wireless-AC 8260". (Please see attached picture). I thought it is a driver issue, so tried to update my ethernet driver, but nope. The same error still exists.
Attachments (1)
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
On my PC the adapter status shown in PLCnext Engineer matches the status shown by the ipconfig command:

2021-09-09_18-41-36.jpg

2021-09-09_18-50-34.jpg

Are you sure there is a network connected to the adapter you want to use?

.
Attachments (2)
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Just to add some new information to this ticket -

It seems that PLCnext Engineer only reads the Ethernet adapter status on startup, so if an adapter is actived after PLCnext Engineer starts, then PLCnext Engineer will only detect the change when it restarts.
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support