Dear PLCnext team,

I have a question about Profibus® Slave support on PLCnext controller.

Would it be possible to support Profibus® Slave on PLCnext controller ?

Our customer is looking for a Profibus® Slave solution that runs on PLCnext controller.
I know that the PLCnext controller act as Profibus® Master with Profibus® extension module which will be released soon.
How about the Profibus® Slave ?

I'd appreciate it if you could give any advice for a Profibus Slave solution.

 

Sincerely,
Hiroki Kannon

Frank PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi Hiroki,

I guess the easiest would be to just use the AXC F IL Adapt 1020304 with an IB IL PB MA 2700630.

The IL PB MA can be used as PB slave and in this mode is also no difficult  configuration necessary (just a dip switch for the data length).

Take care,

Frank


Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support