Hello,

I wanted to start working with proficloud gen 2. However, the device remains offline there. I allready tried to add the device again and I also tried to reset the regtoken of the device.

The device is online in the store, I am able to connect in plcnext engineer and winscp. What could be the problem?

 

Arne

Accepted Answer
Arno PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Dear Arne,

The manual for establishing this connection will be published in the plcnext-community very soon. 

I think that you did not add your user certificate from proficloud.io to a trust store in your PLC, didn`t you?

 

Arno


Phoenix Contact Electronics Headquarter - Support Center

Arne Smets Accepted Answer Pending Moderation
0
Votes
Undo

Proficloud service is also enabled in the wbm....

  1. more than a month ago
  2. Proficloud
  3. # 1
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello Arne,
is your PLC able to reach the DNS?
maybe check your Gateway settings.
Also make sure that the Dateime of your PLC is correctly set.

What PLC and FW are you using?


kind regards,
Oliver

Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support

  1. more than a month ago
  2. Proficloud
  3. # 2
Arne Smets Accepted Answer Pending Moderation
0
Votes
Undo

I am able to reach DNS, gateway seems right.

I allready wrote the system datetime to the plcnext again, did it one more time to be sure but it is not helping.

I am using an AXC F 2152, Firmware 2020.0.1 LTS.

Arne

  1. more than a month ago
  2. Proficloud
  3. # 3
Arno PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi Arne,

Did you set the time of the PLC to UTC or to your system time? 

Do you have some OUT-Port variables in your PLC programm marked as proficloud variables? If no metrics/variables are assigned, then the TSD connection would not be established.

Regards, Arno


Phoenix Contact Electronics Headquarter - Support Center

  1. 3 weeks ago
  2. Proficloud
  3. # 4
Arne Smets Accepted Answer Pending Moderation
0
Votes
Undo

I did both of them. The point is, I can acces the PLCnext variables at proficloud.net, but at proficloud.io i will not have a connection..

  1. one week ago
  2. Proficloud
  3. # 5
Arne Smets Accepted Answer Pending Moderation
0
Votes
Undo

True that! After updating to newest firmware and user certificate it worked!