Store PLCnext CommunityPLCnext on LinkedInPLCnext on Instagram  PLCnext on YouTube Github PLCnext CommunityStore PLCnext Community

  1. xuchuansen
  2. Proficloud
  3. Thursday, 03 September 2020

What is the minimum frequency that we collect data from the device to the Proficloud, and I think the default is now 1 second.

Accepted Answer
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Yes, you are correct, the default sampling period (defined in the file /etc/plcnext/device/Services/ProfiCloud/proficloud.settings.json) is 1 second.

It is not recommended to edit this file, but if you did it would not be possible to set this value lower than 1 ms. However it does not make much sense to have a sampling period lower than the fastest cyclic process on the PLC, e.g. if you are sampling data that is only updated by a 100ms cyclic task, then a Proficloud sampling period of less than 100 ms does not make sense.

Hope this helps.

~ Martin.

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support

  1. more than a month ago
  2. Proficloud
  3. # Permalink
xuchuansen Accepted Answer Pending Moderation
0
Votes
Undo

OK,thanks

  1. more than a month ago
  2. Proficloud
  3. # 1
  • Page :
  • 1


There are no replies made for this post yet.
However, you are not allowed to reply to this post.