Regarding with the communication byte size from twos device not equal
- AXC 2152 [ PND IO = 512 ]
- ILC 131 [PND IO = 256]
Does it possible to communicate each other together ?
Hello,
I think in both cases the Data you mention are the PN Device Data.
You have to use one PLC as a controller for this to work.
Who should be PN Controller?
How many data do you need?
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
Hi Oliver
The PN controller is AXC 2152, ILC 131 is PN device. I try to create the new data type PN_IO_256 but the connectivity still not work. Please suggest if further suggestion !
Hello,
you can modify the IO length in your ILC /PCWorx Project.
And Adapt the IO Length at the Submodule Settings of the PN Device in the PLCnext engineer.
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
For this project PN IO 256 it's good enough to transfer data between 2 device. But from the PN client side AXC 2152 default PN IO is 512.
So I decide to create new PN IO 256 in new datatype worksheet, but the communication is still cannot establish.
Do you have any check list to help me investigate it ?
Hello,
I do not see the problem.
You do not needto change the PN device parameters of the AXC F 2152.
You dont need to touch those if the AXC should be the PN Controller.
1. Change PN IO in the ILC 131 Project to 256 in PC Worx -> Wrie new configuration to device
2. Change PN IO at the PN ->131 Submodule in the PLCnext Engineer to 256 like displayed in my screenshot.
There is nothing else you have to change I think.
Please send me a screenshot of the error you are seeing and your current configuration.
kind regards,
Oliver
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
Hello,
Configuration looks okay.
Now the question is if you assgined the Name "ilc-131-eth-device-1" to your ILC?
What PN error code do you get when your PLC starts?
What can you see in the WBM of the AXC F 2152 PN Diagnostic.
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support
Hello sngonkha,
please try setting it up following these instructions.
Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support