  1. Jason Feusner (I.S.A. Corporation)
  2. PLCnext Technology & PLCnext Controls
  3. Wednesday, 22 July 2020

Does someone have the capabilities to run a GSDML file through the Profibus.com PROFINET GSD Checker?

 

The manufacture provides this file for a Servo Drive but it is failing on import with the error. "Failed to import device AKD-PN_DEVICE. Interface submodule is missing" i have been told it imports to Siemens correctly but at this point i am not sure if it as GSDML file issue or a PLCNext Engineer issue. 


Here is the link to the GSDML file. 

https://drive.google.com/file/d/1W-tS9I5wym9VPyiK8_0dbwdbuCgmXEgX/view?usp=sharing

 

Thank you in advanced.. 

 

 

 

 

 

 

Accepted Answer
Martin PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hi Jason,

The error I get when importing that GSDML file is:

2020 07 24 224109

 

This indicates that the device only supports Profinet version 1.0, while the PLC supports Profinet version 2.2 and above.

~ Martin

 

Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support

Stefan Brinkmann Accepted Answer Pending Moderation
0
Votes
Undo

I have checked the GSDML file with the GSDML checker. There are no errors but one warning (see picture). 

As far as I can see, the used schema of the file is version 2.2 which is very old. Maybe there is a newer version available.

The latest schema version is 2.35.

Attachments (1)
Jason Feusner (I.S.A. Corporation) Accepted Answer Pending Moderation
0
Votes
Undo

Thank you for checking that..    They sent me a 2.35 version..   It imports into Seimens just fine.   But when importing it in to PLCNext Engineer nothing happens.   Nothing in logs.   It acts like it import correctly but nothing. 

 

Am i missing something.   I would think i would get a error if it couldn't import. 

 

Here is the link for it.. 

https://drive.google.com/file/d/1MTN4h6m2X2iduFZfdXEPiWVzTt3qfmgl/view?usp=sharing

 

 

Jason Feusner (I.S.A. Corporation) Accepted Answer Pending Moderation
0
Votes
Undo

Thank you for your quick response.    I knew about the log detail but one of my projects..  The one i am working on gives no log detail of the import failure.   However i did get the log detail in a blank project.   

 