Hi,

I'm trying to connect FL Switch 2308 as a Profinet device with PLCnext F2152 Ver.2020.3.

 

I would like to read the record index of the switch, but I cannot read with RDREC error F008 "Invalid type of a parameter" as following images.

 

I think the parameters are right, the ID = 21(or 0x15), INDEX = 3, MLEN =2.

PNIO_CONFIG_STATUS is as following image;

The process data of the switch can be read.

The Switch is working in Profinet mode.

BF-D is blinking, BF-C is OFF and RUN is ON.

 

Could you let me know what is wrong?

 

Best regards,

 

 

Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello Hue,

can you please attach how exactly your Setup looks like.

What Variable+Type is attached to which input / Output of the RDREC Functionblock.

Do you have the same issues with reading other index as well?

Kind regards,
Oliver

Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support

hue1234 Accepted Answer Pending Moderation
0
Votes
Undo

Dear Olivier,

 

It seems that I cannot insert images. I attached the files.

I tried index 1, 2, 3 and 101 and I had same issues.

 

Best regards,

 

Attachments (5)
hue1234 Accepted Answer Pending Moderation
0
Votes
Undo
 

Dear Olivier,

 

I attached two more files.

 

Best regards,

Attachments (2)
hue1234 Accepted Answer Pending Moderation
0
Votes
Undo

Dear Olivier,

 

I found the mistake of  variable Type and solved F008 error and modified.

 

But , now I have another issue.

The ERROR is "TRUE" and STATUS is "16#DE80B000". Please take a look at attached files.

 

Could you let me know what the code is indicating and how I can solve it?

 

Best regards,

 

 

 

Attachments (2)
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello Hue,

i think this means the index is not supported.
I have contacted the Support-Team of the Switch and asked them how to corectly read this index.

kind regards,
Oliver

 

Phoenix Contact Electronics Headquarter - PLCnext Runtime Product Management and Support