I try to read the vendor name of a PROFINET module with RDREC. The status returns F008 which means "Invalid type of a parameter". I do not see which parameter is wrong.
I will add a screenshot of the code and the module parameters.
Attachments (2)
Accepted Answer
Oliver PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo
Hello Stefan,
what is the Datatype of the RECORD input?
Note that it has to be a Byte Array
Phoenix Contact Electronics Headquarters - PLCnext Runtime Product Management and Support
Stefan Brinkmann Accepted Answer Pending Moderation
0
Votes
Undo
The required datatype is displayed as ANY so I attached a WORD Array. RTFM :D