Hello,

I have a struggle with selecting my data from the plcnext program in PROFIcloud. I selected the 'proficloud' ticks, so the variables should be available.

I've made a query and a visualisation, but in the query I am not able to connect those variables. I've selected the right uuid, but I can't find those variables.

How am I able to do this?

 

Arne

Arno PLCnext Team Accepted Answer Pending Moderation
0
Votes
Undo

Hello,

Can you see the values in the TSD Device Manager (at www.proficloud.net), when you select the device? If not, then check one of the following things:

  • Is the time of your PLC set to UTC  time?
  • Is the Gateway-Adress set correctly?
  • Is your PLC connected to the proficloud (check in the web based Management of your PLC)?
  • Are the selected variables in PLCnext Engineer set as OUT-Ports?

The TSD Service in Profucloud V3 (at www.proficloud.io) is not supported so far.

Regards,

Arno