Modbus TCP Client
Available from firmware 2024.6
From firmware release 2024.6 on, there is a Modbus TCP Client directly implemented into the Automation Runtime Platform (ARP) of PLCnext Technology. This Modbus TCP Client can be configured via the PLCnext Engineer programming software. The implementation depends on the libmodbus open source library, provided by libmodbus.org.
How to configure a Modbus TCP communication
  • Make sure the Modbus TCP Client service is activated on your controller (System services page in the Web‑based Management).
  • Open the PLCnext Engineer software suite (v2024.6 or newer) and start a project from a template for your device.
  • Import the PLCnext Engineer Modbus library:
    • In the COMPONENTS panel, right-click on the Libraries section.
    • Right-click the Libraries folder and select Add Library from the  context menu:
    • From the PLCnext Engineer directory that opens in the Windows Explorer, pick the Modbus.pcwlx library.
      ↪ The Modbus library is copied into your PLCnext Engineer project.
      ↪ A Modbus node becomes visible in the Network section of the COMPONENTS panel:
      Modbus node added
  • To assign the Modbus TCP Client feature to your device, unfold the Modbus → Devices folder stack down to the Modbus TCP Client items:
    The number indicates how many communication lines to Modbus TCP servers can be set up; that depends on the PLCnext Control type running the Modbus TCP Client feature:
    PLCnext Control   maximum Modbus servers
    AXC F 1152 8
    AXC F 1252 8
    AXC F 2152 16
    AXC F 3152 16
    RFC 4072S 16
    RFC 4072R 16
    BPC 9102S 16
    VPLCNEXT CONTROL 1000 8
    VPLCNEXT CONTROL 2000 16
    VPLCNEXT CONTROL 3000 32
  • Click and drag the appropriate item for your PLCnext Control from the right-side COMPONENTS panel over to the left-side PLANT panel and drop it onto the controller.
    ↪ A Modbus TCP node becomes visible (from 2026.0 LTSModbus TCP Client):
  • Double-click the Modbus TCP (or Modbus TCP Client) node in the PLANT panel to open the Modbus Device List tab in the working area.
  • Assign the IP addresses of the Modbus TCP gateways or servers you want to communicate with:
  • To open the Modbus configuration, double-click the according Modbus TCP device in the PLANT view.
    ↪ The Settings page becomes visible:
  • Check and change the default timing parameters for the server connection:
    Swap bytes can be activated if necessary
    Protocol by now, only TCP is available
    Port default is 502
    Connection timeout specifies how long the client waits for a response in this cycle of establishing a connection before a new connection is possible
    Reconnection interval specifies how long to wait for a new attempt to establish a connection
    Response timeout specifies how quick the Modbus server should respond to the client's Modbus telegram; otherwise an error is issued to the diagnostic register
    Trigger rate Cycle time of the telegrams sent to the Modbus TCP server
  • Switch to the Registers tab to set up the Modbus function codes (FC) and data types for your application, e.g.:
    ↪ The function codes are then connected to global variables which you can are also see listed at the bottom of the Data List tab as Process data items.
Once you have set up function codes in the above Registers tab, then you can work with these global variables in your automation programs.
Reference
Info icon Find detailed information and instructions on Modbus TCP configuration by means of PLCnext Engineer in the PLCnext Engineer Online Help for the 2024.6 software release (or newer).
Supported function codes
These are the Modbus function codes (FC) that are supported by the PLCnext Technology Modbus TCP Client:
FC Description
01 Read Coils
02  Read Discrete Inputs
03  Read Holding Registers
04  Read Input Registers
05  Write Single Coil
06 Write Single Register
15 Write Multiple Coils
16 Write Multiple Registers
23 Read/Write Multiple Registers
Diagnostic registers
For each configured Modbus server, PLCnext Engineer creates the defined IN and OUT ports. At runtime, the firmware puts values to the OUT ports and monitors the IN ports.
The diagnostics register is read out and displayed in the PLCnext Engineer diagnostic view:
Process data item Port type Function Data type
IP_ADDRESS OUT IP address of the server as a 32-bit value Unsigned32
UNIT_ID OUT Unit ID Unsigned32
OFFLINE_CNT OUT Counts the number of connection losses Unsigned32
EXCEPTION_CNT OUT Counts the number of exceptions received Unsigned32
EXCEPTION_CODE OUT A single exception code received Unsigned32
EXCEPTION_FC OUT Function code (FC) of the exception Unsigned32
EXCEPTION_REG_ADDR OUT Modbus register address of the exception Unsigned32
AVG_NET_CYCLE_TIME OUT Average update time (in ms) for updating the IO data per server Unsigned32
MIN_NET_CYCLE_TIME OUT Minimum update time (in ms) for updating the IO data per server Unsigned32
MAX_NET_CYCLE_TIME OUT Maximum update time (in ms) for updating the IO data per server Unsigned32
ACTUAL_NET_CYCLE_TIME OUT Update time (in ms) for updating the I/O data per server Unsigned32
STATE OUT Communication status:
If the bit0 value is 1TRUE, then a TCP communication is active.
If the bit 1 value is 1TRUE, then a notice is present and the EXCEPTION_CODE register is set.
Note: Phoenix Contact recommends to read Modbus process data only if the STATE variable has no exception (bit 1 not set) and the EXCEPTION_CODEis 0.(TCP communication is running and no exception is present).
ADDITIONAL_ERR OUT Value range 0x1000 to 0x1fff
Error code 1001 means that the Modbus connection is not reachable.
Value range 0x2000 to 0x2fff:
Internal error - ask Phoenix Contact for support via the Forum
CONTROL_DIAG_STATISTIC IN If the bit0 value is set to 1TRUE, then all diagnostic data of the respective server connection will be reset (time measurement and error code).
If the bit31 value is set to 0FALSE (default), then the server connection will be activated if possible.
If the bit31 value is set to 1TRUE, then the server connection will be disabled.
Known issue
Known for firmware 2024.6 on all supported PLCnext Control devices - fixed with firmware 2025.0:
Invalid and changing input data can occur in the event of a Modbus exception. This error will be fixed with a further firmware release. Meanwhile, as a workaround, process the read data only if the TCP communication is active and no exception is reported. That is true if the STATE variable has the value 16#0001.
Notifications
PLCnext Engineer users will also find the familiar built-in notifications which can contain plain text, such as "connection lost", "wrong Modbus address", or timeout messages.
• Published/reviewed: 2026-07-31  ☀  Revision 099 •