Web-based Management 2:
Diagnostics → PROFINET
Valid from firmware release 2025.0 - for earlier firmware see Diagnostics - PROFINET
On the PROFINET page, you can view information on the controller and the connected PROFINET devices.
From the 2022.0 LTS release on, the vendor-specific PROFINET alarm error codes are downloaded to the controller by means of PLCnext Engineer, along with the corresponding plain texts for the error codes.
The vendor-specific PROFINET error codes and the corresponding plain texts can be imported into PLCnext Engineer by means of FDCML files (Phoenix Contact devices) or by GSDML files (other vendors).
Overview tab
On the Overview tab, you will find information on the current PROFINET function of the controller and its IP settings.
Status area
In the Status area, you can see whether the controller is currently being used as a PROFINET controller and/or a PROFINET device.
Controller details area
The current IP settings of the controller are displayed in the Controller details area.
Diagnostic information on the connected PROFINET devices is available on the Device List tab.
Device List tab
The Device List tab provides an overview of the configured PROFINET devices.
The overview contains the device names of the PROFINET devices, the current IP settings, as well as the diagnostic state and code.
The diagnostic symbols are described in the help panel of the WBM page.
Opening WBM of a PROFINET device
Some PROFINET devices feature their own web-based management (WBM). You can open WBM of a connected PROFINET device via a link on the Device List tab.
- In the Device Name column, click on the PROFINET device whose WBM you want to open.
The WBM of the PROFINET device is opened in the web browser in a new tab.
Opening the Device Information view
In the Device Information view, you will find certain general information, the current IP settings as well as diagnostic information for each connected PROFINET device.
Update frequency for diagnostic data
Diagnostic data is updated with an update frequency of 1/s. The following information is updated:
- Device List: The Device List can be recomposed, e.g., after changing and updating the PLCnext Engineer project.
- Diagnostic data:
- Change of connection status of the PROFINET devices
- Diagnostic state of the PROFINET devices
Tree View tab
The Tree View tab provides an overview of the configured PROFINET devices. The overview contains the device names of the PROFINET devices, their current IP settings, as well as the diagnostic state of the devices and modules.
Tree View
The PROFINET Tree View contains all the PROFINET devices from the Device List.
- Click [+] or [‒] to open or close the next level of the Tree View.
The following icons provide information on the current diagnostic state of the PROFINET device:
| OK | Normal operation state. |
| Warning | Maintenance is required according to the PROFINET specification. |
| Urgent Warning | Maintenance is urgently required according to the PROFINET specification. |
| Error | An error has occurred which needs to be resolved immediately. |
| AR Deactivated | AR is deactivated, e.g. via function block AR_MGT in PLCnext Engineer (from firmware 2022.0 LTS). |
| Module Difference | There is a physically another module in the backplane than in the configuration of the project (see Module difference). |
| No Connection | AR could not be established. |
| No Information | In case of a deactivated or not established AR there is no information available of the actual physical configuration in the backplane of the respective PROFINET device. |
PROFINET diagnostic code reference
The PROFINET page in the WBM Diagnostics area of your controller is used to view information about the controller and the connected PROFINET devices, as well as information about their Axioline F local bus devices. The displayed diagnostic code consists of several bits that are evaluated individually.
The diagnostic state (OK, warning, error) as well as the corresponding diagnostic text are based on an evaluation of the diagnostic bits. The following section is an excerpt from the AutomationRuntimePlatform/Source/Arp/Io/ProfinetStack/Controller/Services/DiagnosticInfo.hpp firmware file. It contains the bit description of the diagnostic code:
The controller may show the error as a hexadecimal code which you need to convert to a binary and read the set bits from there.
Show how to convert hex codes into bitsShow how to convert hex codes into bits
- Conversion from hex to binary
- Convert each hex digit into 4 binary digits and write them down one after the other.
For example, hex codeHex 0123456789ABCDEFBinary 00000001001000110100010101100111100010011010101111001101111011110x24converts to binary0010|0100.
Leading zeros at the binary can be omitted, so go with100100.
- Translation to binary to set/unset bits
- Starting from the right, look up the bit for each binary value
1(meaning: that bit is set).
In the above example with hex code0x24equalling to binary100100, this means: bits 2 and 5 are set.Binary 00000100100Bit Bit 10Bit 9Bit 8Bit 7Bit 6Bit 5Bit 4Bit 3Bit 2Bit 1Bit 0
Meanings and recommendations for action
| Bit | Bit is set if... | Meaning and recommendation for action |
| 0 | not connected | The PROFINET controller could not establish a connection with the PROFINET device or the Application Relation (AR) was deactivated. Please check the Ethernet connection and the PROFINET device name (e.g. with PLCnext Engineer PROFINET Online Devices) In addition, check if the AR has been deactivated in the PROFINET device settings. |
| 1 | data invalid | The PROFINET device is connected to the PROFINET controller, but the device has marked the process data as invalid due to a fault. The process data are not transferred to the process image. Please check the diagnostics of the PROFINET device and contact the manufacturer of the PROFINET device if necessary. |
| 2 | diagnosis is available | The PROFINET device reports a diagnosis. Please check the diagnostics of the PROFINET device and contact the manufacturer of the PROFINET device if necessary. |
| 3 | module difference is available in case of configuration difference | During the initialization of the PROFINET connection, a deviation between the target and actual configuration was detected. Please check the configuration of the PROFINET device. In the default setting of PLCnext Engineer, the connection remains established in the event of a difference in configuration. |
| 4 | AR is deactivated | The PROFINET device is configured in the project, but the AR (Application Relation) has been deactivated. Check the PROFINET evice settings and activate the AR. |
| 5 | neighborhood information is not available | No neighborhood information is available in the network used. This is usually due to the use of components that are not at least PROFINET Conformance Class-B (CC-B) compatible. For a stable PROFINET network, Phoenix Contact only recommends using CC-B or CC-C compliant PROFINET devices. |
| 6 | neighborhood information not unique | In the network used, neighborhood information is available but not unique. This means that more than two PROFINET devices can be detected on one port of at least one switch. This is not permitted and may result in the automatic device exchange not functioning reliably. This is usually due to the use of components that are not at least PROFINET Conformance Class-B (CC-B) compatible (e.g. unmanaged switches). |
| 7 | identify.cnf on alias received, but name of the device is already - configured in another AR | A DCP Identify (Alias) Request was sent to the network. However, the alias name of a device being searched is already in use by an AR. This information is only an indication that the control program is probably trying to establish a connection with a device although a connection is still active. |
| 8 | "Maintenance Required" information is available | The PROFINET device has transmitted a maintenance request (maintenance alarm). Please check the diagnostics of the PROFINET device and contact the manufacturer of the PROFINET device if necessary. |
| 9 | "Maintenance Demanded" information is available | The PROFINET device has transmitted an urgent maintenance request (maintenance alarm). Please check the diagnostics of the PROFINET device and contact the manufacturer of the PROFINET device if necessary. |
| 10 | "Channel or Manufacturer Specific Diagnosis" information is available | Optional and manufacturer-specific information is available. Please check the diagnostics of the PROFINET device and contact the manufacturer of the PROFINET device if necessary. |
| 11 to 15 | reserved | Should always be 0. |
Tutorial video
From release 2022.0 LTS, the PROFINET diagnostic features have been extended as described above.
Note: Tutorial videos are embedded from the Phoenix Contact Technical Support YouTube channel. With playing an embedded YouTube video in this platform, you accept the YouTube Terms & Conditions. Even showing the video previews on this page depends on your personal settings. To watch YouTube videos, you have to allow cookies for marketing purposes which will remain on your device. The data gained through these cookies will be used by YouTube to provide video suggestions and advertisements based on your browsing habits, and that data may be made available to other parties.
| 03m:33s | HDTV 720p | English | English |
| 03m:35s | HDTV 720p | Deutsch | ‒ |