AXC F 1152 

Note: For further information about the hardware, refer to the product documentation of this controller (item no. 1151412):

The AXC F 1152 is approved for certified security based on a limited scope. The AXC F 1152 does not support left-alignable modules and therefore network segmentation is not possible. 

Since no network segmentation is possible, you can only use the AXC F 1152 as a stand-alone controller without subordinate networks.

For information on the security context, refer to the topic Generic Security Concept. 

Connecting and operating elements of the controller

The controller consists of the following components: 

 

SD card

  • Only use encrypted SD cards!

Information on this can be found in the topic SD card encryption.

Security seals

In order to prevent manipulation of the device supplied and to detect unauthorized opening of the device, security seals have been applied to the controller.

From production dates Q2/2022 and later, the housing of PLCnext Control AXC F 1152 is protected by a security seal on both sides like shown below. 

These security seals are damaged in the event of unauthorized opening. In this case, correct operation of the PLCnext Control can no longer be ensured.

  • Check the delivery for transport damage. Damaged packaging is an indicator of potential damage to the device that may have occurred during transport. This could result in a malfunction.
  • Do not open the housing. If the housing is opened, the function of the device can no longer be ensured.
  • Check at regular intervals that none of the seals are damaged. If any of the seals are damaged or missing, it may be that the device has been tampered. In this case, contact Phoenix Contact without delay before using the device.
Example: AXC F 2152 viewed from the left side
Example: AXC F 2152 viewed from the right side

Assignment of the Ethernet interfaces

The following is an overview of how the Ethernet interfaces are assigned on the various pages in the WBM: 

Ethernet interface hardware Ethernet interface WBM - Network page Ethernet interfaces WBM - Firewall page
X2 TCP/IP (LAN1) - Switched Mode
(see Assigning IP addresses)
eth0
(see Configuring extended firewall settings)
X1 TCP/IP (LAN1) - Switched Mode
(see Assigning IP addresses)
eth0
(see Configuring extended firewall settings)

How to reset the controller 

Reset 1

Resetting the controller to default setting type 1 deletes all settings that you have configured. These include, for example:

  • The PLCnext Engineer project, including all applications that have been programmed in accordance with IEC 61131-3
  • All applications that were programmed using high-level languages
  • The configured bus configuration
  • The network configuration of the controller
  • Changes and extensions that you have made to the operating system or to the firmware

To reset the controller to default setting type 1, proceed as follows:

  • Switch off the supply voltage of the controller.
  • After the LEDs have gone out, press the reset button.
  • Hold the reset button down and switch the supply voltage on.
    The RUN and FAIL LEDs light up.
  • Release the reset button.

The controller is reset to default setting type 1.

Reset 2

Resetting to default setting type 2 resets the controller to the delivery state. This deletes all settings that you have configured.

To reset the controller to default setting type 2, proceed as follows:

  • Switch off the supply voltage of the controller.
  • After the LEDs have gone out, press the reset button.
  • Hold the reset button down and switch the supply voltage on.
    The RUN and FAIL LEDs light up.
  • Press and hold the Reset button down (approx. 30 s) until all LEDs (except the E and D LEDs) light up.
  • Release the reset button.

The controller is reset to default setting type 2.

Netload Limiter configuration

You configure the Netload Limiter on the Netload Limiter page in the WBM (Configuration → Network, Netload Limiter tab).

Fur further information, refer to the topic Configuring Netload Limiter.

Controller-specific information on the 62443-4-2 compliance list

Note:  Please note the additional controller-specific information on the 62443-4-2 compliance list.

 

 


• Published/reviewed: 2026-04-20 • Revision 022 •