Security Profile: Activating PROFINET 

A large port range is required for the use of PROFINET as the system automatically selects the required ports depending on the network configuration.
To restrict access to the PROFINET interfaces, the IP addresses of the PROFINET devices must be configured so that only the controller and the device, and possibly also the engineering (supervisor), can communicate with each other.

Note: If you execute the DCP sub-option "ResetToFactory", the communication parameters of the controller are reset (StationName = "", IP = 0.0.0.0, DHCP, PDev parameters). If the information is invalid, PROFINET inserts default values.
  • Use PLCnext Engineer to set the IP addresses and the device name according to your requirements (in the "Online controllers" area).



From the controller perspective, the PROFINET buscoupler must be configured in the firewall as an input rule (Interface and From IP).
The output rule generally defines the ports from which data is sent and the PROFINET buscoupler (To IP) is defined as the recipient of the data.

In the security context in the "Machine" subnetwork, the PROFINET buscoupler has the IP address 172.16.30.30, which must be configured.
Firewall rules for the device, if available (e.g. AXC F2152 as PROFINET device), must be set in the same way.

(See topic Security context for embedding in the wider context and topic Deriving IP addresses for the assignment of IP addresses.)

After you have performed a threat analysis and implemented appropriate protective measures from the security context, you can activate the PROFINET Controller. The PROFINET device is activated by default. 

Note: If you do not use PROFINET device, you must deactivate it.
  • Log in to the WBM. 

    Return to topicHow do I get to the WBM again? Click here for more information... 

    Establishing a connection to the Web-based Management (WBM):

    • Open a web browser on your computer.
    • In the address field, enter the URL https://<IP-address-of-the-controller>/wbm,
      for example: https://192.168.1.10/wbm.

    For further information, see WBM.

  • Open the System services page (SystemSystem services) in the WBM. 
  • Activate the toggle switch of the PROFINET Controller.
     
  • Click the SAVE PAGE & RESTART button.  

After the PLCnext Control has rebooted, you must configure the firewall input and output rules. To do this, proceed as follows:

Input rules

Note: To select the correct interfaces, refer to the corresponding PLCnext Control topic (e. g. AXC F 2152).
  • Open the Firewall page (SecurityFirewall) in the WBM. 
  • Open the IP INPUT RULES tab.
     
  • Add a new rule via the .
  • Provide the following information:
    • Select the interface (refer to the topic AXC F 2152).
    • Select the protocol.
    • Enter the IP address range (refer to the topic Deriving IP addresses). 
    • Enter the target port (here: 34964).
    • Select the action Accept
  • Click the SAVE & APPLY PAGE button. 
  • On the IP INPUT RULES tab, add another new rule via the .
  • Provide the following information:
    • Select the interface.
    • Select the protocol.
    • Enter the IP address range. 
    • Enter a target port (here: 49152-65535).
    • Select the action Accept
  • Click the SAVE & APPLY PAGE button.

Output rules

  • Open the Firewall page (SecurityFirewall) in the WBM. 
  • Open the IP OUTPUT RULES tab. 
  • Add a new rule via the .
  • Provide the following information:
    • Select the protocol.
    • Enter a port (here: 49152-65535).
    • Enter the IP address range. 
    • Select the action Accept
  • Click the SAVE & APPLY PAGE button.
Note: To make sure that all newly applied input and output rules are actively used (even for connections that have already been established), restart the PLCnext Control.

 

 